Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss cylinder thermostat in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
10
Got a prob with a sunvic unishare actuator not operating [opening] for c/h can this be why c/h is being shut down as soon as h/w is satisfied by cyl stat.
 
It sounds like the actuator is moving to mid but not c/h only yeh, as you mentioned the heating "shutting down" once h/w is satisfied. If you have 240v on grey to actuator when h/w satisfied and the valve isn't moving to c/h only then the actuator is shot. If you don't have 240 on grey then the cyl stat is defunct/wired incorectly :)
 