Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss detach the snorkel on a balanced flue in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
187
Hi chaps,

Bit of a bugger today - warm flow Utility 150HE , situated in a garage with a balanced low level flue It has gone sooty so cleaned it up changed nozz etc etc but when doing the flue gas analysis , no matter how much I opened up the air intake I could not get enough air. `the only way I could get satisfactory flue gas readings was to detach the snorkel and let the burner run using air from the garage. Anyone else had similar probs before?


many thanks

dave
 
strictly speaking it isnt a balanced flue either, just a room sealed one if it sucks air in one part and blows the fumes out the other part..
 
Also check that when you turned the Allen bolt air adjustment to make sure the wee air door is sliding open. I see a few of them that the threads have stripped on the bolt inside. Take the spigot off and look inside with a torch. Them RDB air adjustment parts are poor.
Also be sure the flue is correct size for that output - ask Warmflow if not sure. I know a Warmflow 150 utility condensing boiler with balanced low level flue that is tending to soot up and Warmflow had previously said wrong flue for this large a boiler and disconnected snorkel apparently.
 
Last edited:
+1 with best , same with a warm flow utility. , plastic damper wasn't moving when turning Allen key . Stripped down put back together all good then .
 
sorry guys -should have said...the plastic damper was working fine / not jammed ,..so opened up fully
 
thanks for all the input fellas - am I OK to let it run now with the snorkel detached

I would be apprehensive about it if the flue seals are knackered you possibly have pocs being discharged into an enclosed area

maybe run a room test with your flugas analyser to check for any co readings
 
see post 2, if that is the probable issue dont even use the boiler until you have replaced the seals! god almighty mess will await you in a few weeks, plus, if the intake seals are gone you may well kill your customers
 
Status
Not open for further replies.

Similar plumbing topics

Don't think that M.valves will pull in air...
Replies
17
Views
4K
Yes, I did see that the matter of putting Mag...
Replies
18
Views
3K
I
  • Locked
Not in open forum. Read the rules.
Replies
1
Views
909
Dotty
D
Back
Top