Quick question about ventilation for gas fires with cavity wall insulation
We would like to get cavity wall insulation, we chose a CIGA registered installer and have been told we need a vent in our lounge as we have a fire. I have looked at the "CIGA flues, chimneys and combustion air ventilators" guidance and my understanding of it is that under 7kw is fine and doesn’t need a vent unless its a DFE and then it isnt clear other than to consult the manual or seek technical advice.
The installer says that because its a DFE then it will need a vent. It’s a Magiglo Elite 16 fire, which is a 6.9kW DFE fire. I have had a look at their manual and it says it doesn’t need a vent unless it fails a spillage test but doesnt mention cavity wall insulation at all in relation to this- so does this change things?
From my manual:
"For models with heat inputs not exceeding 6.9kW additional ventilation is not normally required in the room that the fire is fitted. However, if spillage is detected during spillage test additional ventilation may be required. In GB reference should be made to BS 5871art 3, which makes clear the conditions that must be met to demonstrate that sufficient ventilation is available"
I've asked the installer about this and they say as its DFE it needs one. They have given me the details of someone to call tomorrow to speak about it further but I wanted to check if I was missing anything. I really don’t want an unnecessary vent, due to concerns about drafts, bugs and aesthetics but understand if I do need one for safety reasons. So if I dont need one and they insist I would consider asking an alternative installer but I feel bad since they spent ages assessing the property to apply for funding etc, and don’t want to waste a second installers time if I’m misunderstanding and they are correct about the requirement.
Any advice gratefully received.
We would like to get cavity wall insulation, we chose a CIGA registered installer and have been told we need a vent in our lounge as we have a fire. I have looked at the "CIGA flues, chimneys and combustion air ventilators" guidance and my understanding of it is that under 7kw is fine and doesn’t need a vent unless its a DFE and then it isnt clear other than to consult the manual or seek technical advice.
The installer says that because its a DFE then it will need a vent. It’s a Magiglo Elite 16 fire, which is a 6.9kW DFE fire. I have had a look at their manual and it says it doesn’t need a vent unless it fails a spillage test but doesnt mention cavity wall insulation at all in relation to this- so does this change things?
From my manual:
"For models with heat inputs not exceeding 6.9kW additional ventilation is not normally required in the room that the fire is fitted. However, if spillage is detected during spillage test additional ventilation may be required. In GB reference should be made to BS 5871art 3, which makes clear the conditions that must be met to demonstrate that sufficient ventilation is available"
I've asked the installer about this and they say as its DFE it needs one. They have given me the details of someone to call tomorrow to speak about it further but I wanted to check if I was missing anything. I really don’t want an unnecessary vent, due to concerns about drafts, bugs and aesthetics but understand if I do need one for safety reasons. So if I dont need one and they insist I would consider asking an alternative installer but I feel bad since they spent ages assessing the property to apply for funding etc, and don’t want to waste a second installers time if I’m misunderstanding and they are correct about the requirement.
Any advice gratefully received.