Like all these things you gotta know which regs to look in
The Gas regs cover the gas pipes etc, IIRC:
BS6891-2005 8.16.2 Separation of installation pipework from other services.
Where installation pipes are not separated by electrical insulating material, they shall be spaced as follows:
a) at least 150 mm away from electricity meters and associated excess current controls, electrical switches or sockets, distribution boards or consumer units;
b) at least 25mm away from electricity supply and distribution cables.
(correct me if I'm wrong)
The other bit comes from the Electrical regs (BS7671 - 2008 +A1 2011) - and there is probably a bit in BS6700 - don't have that one to hand
528.3 Proximity to non-electrical services
528.3.1 A wiring system shall not be installed in the vicinity of services which produce heat, smoke, or fumes likely to be detrimental to the wiring, unless it is protected from harmful effects by shielding arranged so as not to affect the dissipation of heat from the wiring (and CU aka fuse box etc)
528.3.4 Where an electrical service is located in close proximity to one or more non-electrical services,
both the following conditions shall be met:
(i) The wiring system shall be suitably protected against the hazards likely to arise from the presence of the other services in normal use
(ii) Fault protection shall be afforded in accordance with the requirements of section 411
So bottom line:
Gas pipes see gas regs,
Hot pipes, you need to put a barrier/insulate the pipe or move it away.
Cold Pipes make sure they don't leak/ there is no drain cock close to any wiring / the CU
If you have any concerns therefore, some method of shielding the CU (1/2 hour fire resistant board) would be sensible.