do any I you guys fit a pressure test point to gas pipe as close to the boiler as possible?
The reason I’m asking is I’ve been asked to quote to fit a Worcester green star compact 38kw combie boiler, I’ve done my pipe sizing which I hope is correct (approx 15m of pipe including fittings) so I will be upgrading the gas from the meter from 22mm to 28mm. No other appliances connected.
On looking at the MIs they ask for 19 to 23mb from the meter (standard for NG) and a one 1mb drop from the meter to the inlet (standard again) And then a 1.5 mb drop from the boiler inlet to the gas valve.
As far as I know unless you fit a test point under the boiler how can you get the inlet pressure? As the only other reading you can get is from the meter to the gas valve.
I think my pipe sizing should be accurate but I don’t see how I can confirm this with out putting an additional test point on allowing to check for a 1mb drop between meter and appliance.
Forgive me if I’m missing the obvious.
The reason I’m asking is I’ve been asked to quote to fit a Worcester green star compact 38kw combie boiler, I’ve done my pipe sizing which I hope is correct (approx 15m of pipe including fittings) so I will be upgrading the gas from the meter from 22mm to 28mm. No other appliances connected.
On looking at the MIs they ask for 19 to 23mb from the meter (standard for NG) and a one 1mb drop from the meter to the inlet (standard again) And then a 1.5 mb drop from the boiler inlet to the gas valve.
As far as I know unless you fit a test point under the boiler how can you get the inlet pressure? As the only other reading you can get is from the meter to the gas valve.
I think my pipe sizing should be accurate but I don’t see how I can confirm this with out putting an additional test point on allowing to check for a 1mb drop between meter and appliance.
Forgive me if I’m missing the obvious.