Hi Can anyone help with this please? Not sure this thermostat is working properly. I turned it on this morning and temp in room was 21....thermostat set to 23 and heating came on but after only about a minute or 2 it went off!!! I then turned it up to 25 and it then stayed on but obviously had to turn it down once warm enough. Also when temperature in room was saying 23.5 thermostat set to 23 heating comes on a couple of times for just 20 seconds... This was only fitted yesterday and am at the moment having to set the default to 25 to get boiler to stay running then just turn on thermostat off when warm enough... does anyone have any ideas what could be wrong? Thanks
Jane
 
Is it 23 dc in the room where the thermostat is located?
 
When I got up this morning and turned the thermostat on. the room temperate said it was 21 degrees. I had the thermostat set to 23 degrees so when I turned the thermostat on the boiler came on but it did NOT stay on and the temperature in the room was still only 21 degrees. The only way I could get it to stay on was by using the plus button and set it to 25 degrees. It is a Drayton Digistat + 1
 
TBH that sounds like it's working correctly

Normally around 2dc accuracy
 
Maybe I am being silly but how can that be right when room says it is 21 and stat is set at 23. Surely the boiler should stay running until the temp on thermostat is showing the set temp of 23? Also when I look at digital window from an angle you can see colours (like if you get an oil spill you see colours on the top)
 
Also if room stat is set to 23 when the actual temperature is showing 23.5 boulder can come on for about 20 seconds or so
 
Will click on at 25 when the room is 23 correct

Or 20 when the rooms 18 etc
 
Okay thanks.. although I am not sure about it as my friend has same one and hers is fine... also have you heard of the colours on screen?
 
Yes that's very standard with an lcd screen
 
When room temp is say 21 and you turn it up to 23 is the flame symbol displayed above the selected temp of 23 on the left hand side of the display? What boiler do you have?
 
Last edited:
Yes the Flame symbol is there and the boiler is running and rads getting warm just didn’t stay on long enough to get the room temp up to the 23 but when I put it up to 25 the boiler did then stay on. I have a Glowwarm 24cxi combi boiler
 
Remember the boiler can sometimes produce heat faster than your rads can lose it so the boiler has to back off, is it a small system or do you have TRV's turned off or set low?
 
You say also that you boiler fires up for a short time when your heating is off, I suspect you have the preheat feature turned ON, check your manual and turn it OFF, hope this helps.
 
Is only a small system... 1 bed flat 5 rads in total... No it it not the pre heat it does that for the hot water side. I meant that it calls for heat and only stays on for 20 seconds sometimes. Like when temp says it is 23.5 and the thermostat is set at 23
 
Status
Not open for further replies.

Similar plumbing topics

A few decades ago, on-off control with a wide...
Replies
8
Views
719
76 Views and not one single "expert" has...
Replies
5
Views
669
I don't believe moving the manual lever over...
Replies
5
Views
552
I have a home with an oil boiler in a garage...
Replies
0
Views
696
I will have to experiment like you said and...
Replies
6
Views
1K
Back
Top