Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Duo-Tec hot water issues in the Gas Engineers Forum area at Plumbers Forums

Messages
2
Called to repair Baxi Duo-Tec Combi no hot water? Replaced plate heat exchanger blocked solid replaced change over cartridge and DHW sensor still the same issue Boiler comes on reaches 43-45* then shuts down then reignites and then same again? I took the inner door panel off while the hot tap was running the boiler fired up and stayed on the hot water reached temperature? When refitting the inner door the water temperature dropped back down to the 43-45* and kept recycling? Cleaned the Venturi the sensing tube checked the vertical flue for blockages it’s clear put everything back together still the same problem? Central heating working ok just issues with hot water. Just so stumped!!!!!!
Any advise welcome.
 

Similar plumbing topics

  • Question
If it’s definitely E28, i‘d get your engineer...
Replies
1
Views
806
Deleted member 120897
D
The OP mentioned that he has a "Vailant home...
Replies
6
Views
1K
Are you Gas Safe Registered? If not please...
Replies
2
Views
534
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
857
HRP123
H
Back
Top