Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss ECV letby on boiler install job in the Boilers area at Plumbers Forums

Status
Not open for further replies.

jaydebruyne

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,718
hi peeps,

Just tested the gas pre boiler install and the ECV is letting by. Obv I won’t know if there’s a drop on the system until the ECV is replaced, do I halt the install until this is done or carry on cuttinggas pipe so I can take the oldboiler off?

Cheers
 
Have you phoned it in ?
 
Anyone ever replaced a Keston with a new Keston and joined into the existing twin flue?????
 
Yea needs to be the right stuff, but I think you have to pressure test the flue to make sure it's sound
 
Yea needs to be the right stuff, but I think you have to pressure test the flue to make sure it's sound
How do you pressure test it? Sean can you give me a bell please as I need to order the Keston in next 30 mins
 
How do you pressure test it? Sean can you give me a bell please as I need to order the Keston in next 30 mins

Air test it like drains
 
Where do they exit on the property?
 
The roof I think as can’t see them coming out the external walls

Need to check it's supported and terminal is correct etc

Also need to put your bung in it
 
Need to check it's supported and terminal is correct etc

Also need to put your bung in it
Yeah ... jobs been a nightmare today!
Just trying to think where I could get a pressure test kit?????
 
upload_2018-2-15_17-9-52.jpeg


Nothing like this ?
You must be able to make something up?
They're both open ended so it doesn't need to be a big pressure just as Shaun said, a quick drain test will do.
 
Status
Not open for further replies.

Similar plumbing topics

sweet. that is the answer i was hoping for!
Replies
4
Views
81
Time and make a note of how long the boiler is...
Replies
1
Views
535
No they just do the address, thank goodness...
Replies
8
Views
1K
Normal as they only get paid 150-200 per install
Replies
11
Views
2K
S
Nothing other than a pain to work on not...
Replies
1
Views
626
Back
Top