High Zs on auxiliary circuits
Hi
I have a distribution board controlling conveyor belt in which all auxiliary circuits for start/stop switches, emergency buttons, etc are supplied through 230V/230V separating transformer.where secondary winding is earthed on one end. I've got high Zs readings for all those control circuits (~20Ohms) protected by 2Amp circuit breakers
It's 230V so low voltage fixed installation requiring inspection and testing with 0.4s disconnection time (TNC-S). Can't find anything in the regs how to treat this situation. Would it be departure due to DB manufacturer design?
High Zs on auxiliary circuits for more information
You may reply to this message here.
Hi
I have a distribution board controlling conveyor belt in which all auxiliary circuits for start/stop switches, emergency buttons, etc are supplied through 230V/230V separating transformer.where secondary winding is earthed on one end. I've got high Zs readings for all those control circuits (~20Ohms) protected by 2Amp circuit breakers
It's 230V so low voltage fixed installation requiring inspection and testing with 0.4s disconnection time (TNC-S). Can't find anything in the regs how to treat this situation. Would it be departure due to DB manufacturer design?