Went to service this Duo Tec today, thought, nice quick job, just a boiler in and out within 30 mins. Wrong.
Boiler was noisy on start up, the FGA confirmed my thoughts. Before pulling the flue apart I checked the condense trap, checked the heat exchanger and did the FGA on minimum with the combustion door open, which caused the boiler to operate a little better.
Pulled the flue apart in the loft and found the exhaust cracked. I think this is about 4 I've come across now. But this boiler was only fitted 32 months ago. It always seems to be the first flue extension and appears to be where the spring keeps the gap between the outer and inner flue. The crack gets worse and worse, until, like this one, it forms a hole and allows a mix of products and air to create huge quantities of CO.
Boiler was noisy on start up, the FGA confirmed my thoughts. Before pulling the flue apart I checked the condense trap, checked the heat exchanger and did the FGA on minimum with the combustion door open, which caused the boiler to operate a little better.
Pulled the flue apart in the loft and found the exhaust cracked. I think this is about 4 I've come across now. But this boiler was only fitted 32 months ago. It always seems to be the first flue extension and appears to be where the spring keeps the gap between the outer and inner flue. The crack gets worse and worse, until, like this one, it forms a hole and allows a mix of products and air to create huge quantities of CO.