Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Expansion vessel deflated. in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.

mutley racers

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
5,168
i was called to an alpha cb50 today. The pressure had been gradually decreasing and all of a sudden it became faster. I check the prv pipe and it had was not dripping but water was in the pipe and a little wet patch on the floor. So get to the expansion vessel and no charge what so ever. So i pump it to .8bar as I could not find in instructions what pressure to put in it. so i wack heating on it it rises from 1.2bar to 2.5bar. The aav by the pump has all limescale coming down from where it has been leaking. Do you reckon it is too small this vessel and I should tee one into the return?
 
Hi Mutley, was the vessel just deflated or could the diaphragm be ruptured?
 
Have you checked the pipe feeding the vessel is not blocked? If its a flexi it is easily enough popped out and cleaned.
 
well there was no water present when i pressed the shraeder valve. I don't think it's on a flexi. Think rigid
 
ah ha, i just found in the manual that the vessel should be charged to .5bar. Whoops. And here it says that you should fill system to 1bar and To
check correct operation of the expansion vessel(s) the system pressure should not be more than 2.5 bar when the system is at
maximum operating temperature... Which is what I had. So are they saying it is normal for it to rise 1.5 bar when heated??
 
oh alpha man, i see you deal with alphas. awesome. so all seems fine then with the vessel then? It is rising as it should?
 
If the house/ system is on the large side, an additional vessel might be needed!

Just check the air valve in the vessel isn't leaking, pressure will rise upto and around the 2 bar mark on these, which is very normal.
 
Check the Shraeder valve isn't weaping, most of the CB range do!
 
i was meant to while i was there but totally forgot. I also left my leak detection fluid in the house. So, if it has not fixed the fault, i shall go back and collect fluid and spray valve. Cheers alpha man
 
i was meant to while i was there but totally forgot. I also left my leak detection fluid in the house. So, if it has not fixed the fault, i shall go back and collect fluid and spray valve. Cheers alpha man

just spit on it :devilish:
 
Status
Not open for further replies.

Similar plumbing topics

B
Context for issue: I'd like to start by...
Replies
0
Views
561
Butchy10
B
Pin hole leak on suction side of pump.
Replies
1
Views
467
That means you have a leak as the system...
Replies
9
Views
818
Don't think that M.valves will pull in air...
Replies
17
Views
4K
Thanks mate. No I wasn't aware. I'll get...
Replies
5
Views
3K
Back
Top