Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Expansion vessel size large system in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
S

slide

Have seen many differing formulas for this.

My system volume is 1417 litres
My static head is 11 metres
PRV set at three bar

One calculation I found said it should be 145 litres... can you imagine?
Another said 50, which seems more realistic!

Cheers
 
That one hell of a system over 300 gallons, how big are the boilers
 
Wow thats one mutha of a system.
Almost 1.5 tonne of water...

Whats it in......2 bed semi :eek:
 
Last edited by a moderator:
So 150l then . Some expansion going to occur don't want the gaskets flexing on the groundfloor cos plant rooms on roof and fitted with 12l vessel?
 
A rule of thumb from an expansion vessel/pressurisation unit pump supplier I was told to go by if your stuck on a Commercial job is 1 litre per kW once it's not a high temp heating system. Then go up to d next size up. In your case 100litres.
Should do ye. Did I read ye have d system pressure is set at 3 bar. Maybe I read it wrong, that's a bit too high for 2 storey block. 1.5 bar should be plenty
 
The (Domestic - I know) Heating Design guide says @ PRV 3bar and 1.5bar initial charge = 0.156 * 1417 = 221 Litres

We regularly install 100 litre expansion vessels on systems with a 500 litre buffer tank.

Your expansion factor at 70° Average temperature is 2.2%, and the minimum recommended is 3% .

150 Litres is what I'd go for.
 
System water content = 1500 ltrs
Maximum water temperature = 80°C
Maximum allow working pressure = 3 barg – 0.3 barg
Initial system pressure = 10 mtr static = 1 barg + 0.3 barg


Expansion vessel efficiency = 3.7 – 2.3 = 0.38/3.7


Vessel size = 1500 + 10% X 0.03 = 49 / 0.38


130 ltr

nearest heating vessel. 150 ltres

Bet he's done it by now

BTW Expansion vessels are cheap if you fit one too big what the hell, if you fit one too small you will end up fitting another one along side it and you will look daft
 
Last edited by a moderator:
Status
Not open for further replies.

Similar plumbing topics

Again, without an idea of system volume we're...
Replies
16
Views
4K
  • Locked
Thanks all, particularly Chuck, that was just...
Replies
6
Views
4K
no just work it the same eg 1l and that’s fine
Replies
4
Views
64
  • Question
Hi Mick, Had a quick look at the model 1000...
Replies
5
Views
2K
Back
Top