Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Expansion Vessel Underfloor Heating - Advice in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.
K

kozmian

Hi everyone,

This is my first post - so glad to find somewhere that i will get good advice.

I am about to order an UFH system that I will install myself. I am told by the company selling the components that there will be 60L of water in the pipework and to run it at 60 degrees C. The boiler that i am having fitted has a 7 litre expansion vessel - is this sufficient to cope with the expansion and if not how big does the expansion vessel need to be?

Thanks for your help / advice

Ralph
 
For 60 litres of water @1.5 bar the vessel size works out at 5.1 litre. @1 bar it would need 3.88 litre. You should be ok.
 
Thanks for that - couldn't find a calculator online anywhere!

Had that confirmed by the UFH company as well.

cheers
 
For 60 litres of water @1.5 bar the vessel size works out at 5.1 litre. @1 bar it would need 3.88 litre. You should be ok.


Hi Tamz, would love to know the formula for working this out myself, is there an online calc. or do you think you could post the formula, cheers matey!!!
 
V= eC
______
1-p1
__
p2

V The total volume or nominal size of the expansion vessel.
C The total volume of water in system (60l)
p1 The fill pressure in Bar (1.5Bar) + 1 bar
p2 The setting of the expansion/pressure relief valve in Bar absolute amospheric. (Gauge pressure plus 1 bar)
e The expansion factor (0.03) approx

V= 0.03x60 V =1.8 V= 1.8 V= 4.8
_________ ______ ________
p1= 1.5+1 1- 0.625 0.375
__
p2= 3+1 4


4.8l expansion vessel
 
Last edited by a moderator:
Worked out same as Eco. Slightly different result as different expansion factor used.

V=__eC__
1-P1/P2

=0.0324 x 60
1 - 2.5/4.5

=1.944
1-0.625

=1.944
0.375

=5.184 litres @ 1.5 bar fill pressure
 
Status
Not open for further replies.

Similar plumbing topics

R
thanks mate.
Replies
3
Views
2K
rahul sood
R
I started a long winded response but deleted...
Replies
1
Views
733
S
It’s Possible yes as it’s just filled with...
Replies
1
Views
2K
Probably best to call Worcester Bosch to see...
Replies
1
Views
1K
Back
Top