ive fitted quite a few boilers now but would like to get a bit of experience with fault finding, ive a customer with a boiler that when you get it to 1bar, it heats up and works, but then goes up to over 3bar, blows off, and when cools drops to about half a bar, is this going to be the expansion vessel? or could it be something else? cheers for any advice guys.
 
Expansion vessel lost it's charge pressure.You may get away with re pressurising but it's likely to need replacing.
 
Or......maybe the E/V is ok and the link hose/pipe to it is chocked with gunk.
In most cases though, as mentioned, the E/V lost its charge.
What boiler is it?
 
But before you do anything check that the filling loop isn't passing!
 
no nead to strip down the boiler to fit an expansion vessel just fit an external vessel in a conveniant place along the heating pipework
 
You will also notice that when filling from 0.5 to 1-1.5 bar will happen really quickly, it will be a second or so filling rather than a lot longer
 
Sounds like it needs an additional expansion vessel. How many rads?
 
Status
Not open for further replies.

Similar plumbing topics

it is brand new ( 6 months old ) Worcester gas...
Replies
2
Views
737
losing pressure
L
A
As above 1 bar is more than enough vallants...
Replies
2
Views
671
Thank you - and thank you for pointing that...
Replies
4
Views
1K
The digital does generally overread, also they...
Replies
5
Views
1K
just about to do that, WORCS bosch say fit...
Replies
3
Views
1K
Back
Top