Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Expansion Vessels in the Central Heating Forum area at Plumbers Forums

Status
Not open for further replies.

cr0ft

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,311
Quick one folks. I have a spare potable water expansion vessel kicking around our unit. Rather than skip it, I was wondering if I can use it for a sealed CH circuit? I know you can't do it the other way round but my understanding is potable water expansion vessels are built to a better standard, i.e. mould resistant membrane. What do you guys reckon? If in doubt I will chuck it in the skip but would prefer not to waste it tbh.
 
Can't see any problems with using on heating system.

You may have to check the charge - might be too high for heating system
 
If you use it in your unit you could say it's for training!
 
I think you can use it for a heating system no problem.
It will mean the water is not in contact with the metal vessel, as the potable vessels membrane is normally basically a balloon for holding the water side. So better than a heating vessel as yours won't corrode while membrane remains intact.
I would never bin it anyway as must be worth twice what an ordinary heating vessel costs.
As oz-plumber said, you will need to reduce the precharge to suit your heating system, - normally I do the precharge at 1 bar and keep system fill charge at little more cold for most ch systems
 
Last edited:
check the operating temperature for the diaphragm, potable may be lower than a heating one, heating vessels are only usually rated to 70 degrees
 
I think some potable 1s can't take high temperatures. Just check d label!!
 
Status
Not open for further replies.

Similar plumbing topics

I suppose shouldn't be too surprised as water...
Replies
18
Views
4K
  • Question
Hi Mick, Had a quick look at the model 1000...
Replies
5
Views
2K
no just work it the same eg 1l and that’s fine
Replies
4
Views
59
Back
Top