R

RPG 80

Studying for CCN1 next week. I'm using my NICEIC book going through some old test papers from my foundation course. And Im a bit stumped on this one.

where an extract fan is in the same room as an air brick providing air for combustion?

(a) an additional 50cm2 should be added
(b) the fan must be disconnected
(c) the fan can only blow inwards
(d) an additional 100cm2 should be added

I've read through my book and browsed part J regs also asked my m8 who's gas safe, who gave me an answer which wasn't in the above listing. Any ideas gratefully appreciated.
Cheers RPG
 
As a general guide add an extra 50cm2 will be sufficent for most situations , but installation should be carefully checked.

From bpec domestic gas safety manual.
 
Studying for CCN1 next week. I'm using my NICEIC book going through some old test papers from my foundation course. And Im a bit stumped on this one.

where an extract fan is in the same room as an air brick providing air for combustion?

(a) an additional 50cm2 should be added
(b) the fan must be disconnected
(c) the fan can only blow inwards
(d) an additional 100cm2 should be added

I've read through my book and browsed part J regs also asked my m8 who's gas safe, who gave me an answer which wasn't in the above listing. Any ideas gratefully appreciated.
Cheers RPG
Usually, the recommendation is adding 50cm² to offset any room fans etc. Only through testing can this be confirmed. Usually a window is cracked open slightly to simulate for testing purposes.
A poor worded question.
 
Usually, the recommendation is adding 50cm² to offset any room fans etc. Only through testing can this be confirmed. Usually a window is cracked open slightly to simulate for testing purposes.
A poor worded question.

haha, or a poorly worded question
 
Status
Not open for further replies.

Similar plumbing topics

H
  • Locked
  • Question
Ps if your floor has no insulation it can't be...
Replies
12
Views
2K
Gray0689
G
S
  • Locked
  • Question
We've recently moved to a new house and the...
Replies
0
Views
2K
splobber
S
Back
Top