Good day
I’ve had three heating engineers look at the symptoms that follow to no avail. One of them replaced the electrodes ( part 5110992 )
Boiler: Potterton Promax HE Plus (SL) (2008)
Hot water tank: Heatrae Sadia Megatech Solar 190 Indirect (2008)
Thermostat: Nest 3rd Gen (2017)
Symptoms: (this started in December 2018 with no obvious trigger) an example from this morning, the hot water schedule turns on at 07:00 at which point the boiler turned on and did it’s thing for about 20 minutes. No hot water was used for the next 90 minutes. The call for hot water came in again and the following took place for the next 15 minutes:
The boiler goes through its startup routine, flame comes on, 5 second later it cuts off. Rinse and repeat for 10x+ iterations before it finally stayed on for 2 minutes after which the call for hot water disappeared.
No lights come on the PCB at the time of cut off to suggest there’s anything wrong.
the behaviour isn’t unique to hot water but with hot water this false start routine happens almost always. With heating it happens about 10% of the time.
The PCB was replaced April 2017. No other work happened between that and the electrodes being replaced.
As I said I had three heating engineers looking at it no avail. A lot of shrugging and head scratching turns into a phone call to a colleague but nothing comes out of it.
one heating engineer checked the resistance on the PCB and stated that electrically it is in order. That same engineer suggested that it’s a faulty gas valve inside the boiler(?) that displays the symptoms when the boiler is cold. That sounded odd considering heating does not trigger such behaviour as much as hot water but I don’t know anymore.
Any help would be truly appreciated as hearing the boiler fail to stay on is driving me mad on a daily basis. Thank you.
I’ve had three heating engineers look at the symptoms that follow to no avail. One of them replaced the electrodes ( part 5110992 )
Boiler: Potterton Promax HE Plus (SL) (2008)
Hot water tank: Heatrae Sadia Megatech Solar 190 Indirect (2008)
Thermostat: Nest 3rd Gen (2017)
Symptoms: (this started in December 2018 with no obvious trigger) an example from this morning, the hot water schedule turns on at 07:00 at which point the boiler turned on and did it’s thing for about 20 minutes. No hot water was used for the next 90 minutes. The call for hot water came in again and the following took place for the next 15 minutes:
The boiler goes through its startup routine, flame comes on, 5 second later it cuts off. Rinse and repeat for 10x+ iterations before it finally stayed on for 2 minutes after which the call for hot water disappeared.
No lights come on the PCB at the time of cut off to suggest there’s anything wrong.
the behaviour isn’t unique to hot water but with hot water this false start routine happens almost always. With heating it happens about 10% of the time.
The PCB was replaced April 2017. No other work happened between that and the electrodes being replaced.
As I said I had three heating engineers looking at it no avail. A lot of shrugging and head scratching turns into a phone call to a colleague but nothing comes out of it.
one heating engineer checked the resistance on the PCB and stated that electrically it is in order. That same engineer suggested that it’s a faulty gas valve inside the boiler(?) that displays the symptoms when the boiler is cold. That sounded odd considering heating does not trigger such behaviour as much as hot water but I don’t know anymore.
Any help would be truly appreciated as hearing the boiler fail to stay on is driving me mad on a daily basis. Thank you.