Ferroli domicompact f24b f5 fault | Plumbing Jobs | The Job-board | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Ferroli domicompact f24b f5 fault in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

Hobo128

Gas Engineer
Messages
292
Today I have been to said boiler and when running the tap or central heating the f5 fault pops up.
THis happens after a minute or do. I took the combustion case of and ran thd tap again and it worked with no fault. Put the case back on and it gave me the f5 fault. Didn't have much time to start looking proper but I'm guessing blocked fan venturi.

Has anyone had this problem, can anyone make thus one a bit of an easy Tuesday morning for me.

Cheers
 
Okay, sorted thus out now. Turns out it was the rubber collar that connects the flue inside the boiler had slipped up blocking the air intake hence only working when the casing was off. Repositioned the seal and serviced the boiler including removal of the fan and gave it a clean. Works fine now.
 