beesley121
hi guys,
got called to a ferroli modena 80. will not fire up on hw or heating
on powering the boiler with heating on demand, the pum runs but nothing else. neon 5 flashes indicating low pressure, pressure is fine but bypassed pressure switch to make sure. still nothing. bypassed fan pressure switch, still nothing.
then noticed after a bit more tickering, that neon 5 stayed lit (POWER SUPPLY FAULT). checked power to fan, 47V, obviously not right, should be 230/240v and pressure switch was 13v, not sure if this is right or wrong for this boiler
im thinking pcb but i really dont wanna be wrong on this one
any advice