I.Cannon
Heating works fine, hot water never gets to full temperature, eventually runs cold. If the hot water is ran for long enough it will eventually get lukewarm then back to cold and repeat the cycle, never getting fully hot nor fully cold.
When running the hot water, it slowly gets hot but never to the temperature set to (I've tried setting to both min and max water temperature, neither made any difference). The water then slowly cools to barely above that of the cold water tap.
Temperature readout on the boiler is accurate, the boiler knows the water isn't hot and never reaches 40 degrees celsius. Something is clearly making it shut off early. The burner can also be heard to lower and stop heating the water.
Replaced domestic heat exchanger
Fitted a replacement flow meter.
Boiler is only just over 5 years old and just out of warranty by 2 months, so sadly I'm out of luck on free repairs.
It could be the diverter but it doesn't seem to be as far we can tell.
My Father is the plumber gas safe registered etc, I'm just posting on his behalf, kinda, as it's my boiler.
When running the hot water, it slowly gets hot but never to the temperature set to (I've tried setting to both min and max water temperature, neither made any difference). The water then slowly cools to barely above that of the cold water tap.
Temperature readout on the boiler is accurate, the boiler knows the water isn't hot and never reaches 40 degrees celsius. Something is clearly making it shut off early. The burner can also be heard to lower and stop heating the water.
Replaced domestic heat exchanger
Fitted a replacement flow meter.
Boiler is only just over 5 years old and just out of warranty by 2 months, so sadly I'm out of luck on free repairs.
It could be the diverter but it doesn't seem to be as far we can tell.
My Father is the plumber gas safe registered etc, I'm just posting on his behalf, kinda, as it's my boiler.