Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Flue problem / building control in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

E4gas

Plumbers Arms member
Plumber
Gas Engineer
Messages
564
I fitted a gas fire 3 months ago , run the flue to outside , I got a call from building control that the cast rain water pipe is too close too my flue , I went back to investigate , to find this image.jpgimage.jpg
 
was the hole/ slot there for the outlet?
 
if the rain water outlet appeared after you installed, aint your problem

On the flip side if the valley gutter was already in place but they hadn't fitted the hopper you shouldn't have fitted the flue their?

Seems pretty obvious what was going to happen n
 
The builders had cut groove in wall, and put gully underneath ,
when I was there it was just a flat wall ,

Not sure what's next move , it's a cast iron pipe going near the air intake ,,
 
The builders had cut groove in wall, and put gully underneath ,
when I was there it was just a flat wall ,

Not sure what's next move , it's a cast iron pipe going near the air intake ,,

sorry mate but its your fault and you should of asked whats the notch/ slot was for looks like you will be moving the flue :(
 
The original builders walked off ,
When I was there , there was no one on site who spoke English ,

As stated it was a flat wall , no sign off rain water pipe being fitted there , I'm not that bad not to notice cut out in parapet
 
The builders had cut groove in wall, and put gully underneath ,
when I was there it was just a flat wall ,

Not sure what's next move , it's a cast iron pipe going near the air intake ,,

You should've spotted that, but in your defence. It wasn't there when you did it, your of the hook dude.
 
They cut it out two months after I fitted fire ,, there's no where else it can go ,
 
The original builders walked off ,
When I was there , there was no one on site who spoke English ,

As stated it was a flat wall , no sign off rain water pipe being fitted there , I'm not that bad not to notice cut out in parapet

should of done more digging hay ho its been done now, now you either have to move the flue or find/make a bigger hopper and put the outlet on the left in-line with the pipe
 
Wots the minimum distance for that make of fire E4gas to rain water pipe that they need, can the hopper be moved up as high as it can go or is it a no go ?
 
Ignore me I just looked at pic again , whole pipe too close soz
 
Ignore me I just looked at pic again , whole pipe too close soz

It's a new cast iron down pipe , it's near the air intake, can't see it ever see it damaging the pipe ,

I think it's NCS ,,
 
Can you get a hopper made with a side outlet, not bottom
Don't know if it'll still be too close though even then
 
If that parapet wasn't cut and the copings and render were continuous when you fitted the fire, then in my eyes you're fine (better if you had photos or witnesses)
I'd tell the customer and building control that I would help them any way I could but, all my time/materials would be chargeable
I would say NCS as it is
 
If that parapet wasn't cut and the copings and render were continuous when you fitted the fire, then in my eyes you're fine (better if you had photos or witnesses)
I'd tell the customer and building control that I would help them any way I could but, all my time/materials would be chargeable
I would say NCS as it is

Agree totally, tell them get the builder back, let him sort his mess out.
 
am I missing something most balanced flue fires come with a short flue 1m max . that is high for a fire and from what I can see near ceiling height on a flat roof
 
am I missing something most balanced flue fires come with a short flue 1m max . that is high for a fire and from what I can see near ceiling height on a flat roof


The fire is set under the tv, it's fitted in fire proof wall & fitted to manufactures instructions
 
have you got a link to the manual a fire like that could be ideal with a customer I have
 
Status
Not open for further replies.

Similar plumbing topics

It seems to be a case of having to watch and...
Replies
8
Views
667
Atag let you go for the 600mm clearance away...
Replies
9
Views
860
Fair point. There is a dearth of heating...
Replies
9
Views
1K
Hi, thank you for the reply. It's confusing...
Replies
2
Views
722
Back
Top