Here it is, from current BS
BS 5440-1:2008
Flueing and ventilation for gas appliances of rated input not exceeding 70 kW net (1st, 2nd and 3rd family gases). Specification for installation of gas appliances to chimneys and for maintenance of chimneys
5 General
...
5.2.2 Location of chimney outlets in relation to basement
areas, light wells and retaining walls
Chimney outlets shall be sited so as not to discharge within the curtilage or confines of any enclosed basement area, light well or external space formed by a retaining wall or passage unless provision is made to ensurethe safe dispersal of flue gases as follows.
a) Chimney outlets from room-sealed appliances and fanned draught non-room-sealed appliances may be sited in such areas provided that they are sited not more than 1 m below the top level of the basement area, light well or retaining wall.
b) Chimney outlets from room-sealed appliances and fanned draught non-room-sealed appliances may be sited in a basement area or light well where this is formed by a single retaining wall that creates an uncovered passageway at least 1.5 m wide. This shall
only be done if the passage allows free air circulation beyond and around the ends of the structure and the retaining wall, if the passageway terminates at or above ground level and if
unobstructed air movement can take place at the open ends of the passageway.
Check MI though, hope it helps.