Flushing system before commission | Plumbing Jobs | The Job-board | Plumbers Forums
  • Welcome to PlumbersTalk.net

    Welcome to Plumbers' Talk | The new domain for UKPF / Plumbers Forums. Login with your existing details they should all work fine. Please checkout the PT Updates Forum

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

American Visitor?

Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Flushing system before commission in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

bassmonster

Plumbers Arms member
Plumber
Gas Engineer
Messages
562
Hi all,
As per title, what's the procedure for flushng newly installed central heating and cold feed. Is a powerflush machine needed? Does the boiler need to be part of the flushing? Another Gsr said the just filling up the the system for central heating then draining is enough and for cold feed, just leave the taps open for a while?
 
Hi all,
As per title, what's the procedure for flushng newly installed central heating and cold feed. Is a powerflush machine needed? Does the boiler need to be part of the flushing? Another Gsr said the just filling up the the system for central heating then draining is enough and for cold feed, just leave the taps open for a while?

Depends where your working but last time I looked it was advised that power flush on brand new install, although for me stick a bottle of system cleaner in for a few hours drain and flush, and just let the cold/hot taps run full bore for a few minutes
 
as above and on site it normally doesnt happen
 
Full powerflush while the old boiler's off, if not, get someone else to fit your boiler matey!
No point going in cheap on a job then failing their warranty for them with dirty water; Glow-Worm have now upped their minimum water standard they need to find if called out....

While we're on the subject, don't really think much of the Magnacleanse option..
 
A brand new heating system?
A chemical flush should be enough.
 
Full powerflush while the old boiler's off, if not, get someone else to fit your boiler matey!
No point going in cheap on a job then failing their warranty for them with dirty water; Glow-Worm have now upped their minimum water standard they need to find if called out....

While we're on the subject, don't really think much of the Magnacleanse option..


Magnacleanse is a lot better than no option
 
Full powerflush while the old boiler's off, if not, get someone else to fit your boiler matey!
No point going in cheap on a job then failing their warranty for them with dirty water; Glow-Worm have now upped their minimum water standard they need to find if called out....

While we're on the subject, don't really think much of the Magnacleanse option..


Magnacleanse is a lot better than no option
 
on a new system your only looking to remove swarf, flux and solder so the chemicals will disperse the flux and a standard mains flush done sequentially through the system would bin the rest no problem, anyone saying a powerflush is required has simply forgotten why a powerflushing machine was invented in the first place. As an afterthought a magnacleanse wont achieve anything either.
 
For a whole new system chemicals for a couple of hours or overnight the flush, fill, drain, fill with inhibitor.

New boiler on old system as long as the water doesn't come out black chemicals for a week or 2 before hand, then flush as normal.
 
Never he any issues with a manual flush and a Magna clean.
 
For a whole new system chemicals for a couple of hours or overnight the flush, fill, drain, fill with inhibitor.

New boiler on old system as long as the water doesn't come out black chemicals for a week or 2 before hand, then flush as normal.

Thats one of the reasons why a combi swap takes at least 2 days to do properly
 
Where's Adam, he can get them done in a morning.
 
Status
Not open for further replies.

Similar plumbing topics

Thanks for the science suggestion, I have just...
Replies
12
Views
1K
Hello, I live in a two floor semi with a...
Replies
0
Views
764
Thanks for your response mate. Im not...
Replies
2
Views
673
O
Have you tried waggling the pin on the trv...
Replies
1
Views
909
Thanks for the reply, I followed your advice...
Replies
2
Views
1K
Back
Top