Elderly customer with a 10 rad system. Last 2 rads on system (downstairs) were not getting hot at all. Has contract with BG, they came round, turned off some rads upstairs and downstairs all got hot but said needs powerflush and new pump.
Powerflush carried out then rads were worse.
Most not getting to temperature.
Called me. I was unable to change pump speed on apha2.
Put new pump in, everything heating up. Sorted.
Or so I thought, called back this morning last rad on system lukewarm at best. Couple of other rads not reaching a decent temp.
Some rads upstairs have trv's rest of rads no trv's.
Boiler is new. Pump is new.
Its not a big house, cold feed not blocked.
All the rads have been red hot all at the same time and run fine for 2 days.
It is a very old system. Possibly 50 years old.
On the top floor there is a bedroom cupboard, I removed a panel and found what is like another loft space above the living room. This is where there are heating pipes coming from under the bathroom floor, feeding the bedroom, and drops down for the last 2 rads on circuit
This is all in 15mm. The last 2 rads, the flow pipe is piping hot but not getting through the rads.
This might sound a bit vague but does it sound like a balancing issue or a pipe size issue or something else?
I have left them a couple of small heaters as I didnt have time to investigate fully tonight but hoping to get back saturday.
Powerflush carried out then rads were worse.
Most not getting to temperature.
Called me. I was unable to change pump speed on apha2.
Put new pump in, everything heating up. Sorted.
Or so I thought, called back this morning last rad on system lukewarm at best. Couple of other rads not reaching a decent temp.
Some rads upstairs have trv's rest of rads no trv's.
Boiler is new. Pump is new.
Its not a big house, cold feed not blocked.
All the rads have been red hot all at the same time and run fine for 2 days.
It is a very old system. Possibly 50 years old.
On the top floor there is a bedroom cupboard, I removed a panel and found what is like another loft space above the living room. This is where there are heating pipes coming from under the bathroom floor, feeding the bedroom, and drops down for the last 2 rads on circuit
This is all in 15mm. The last 2 rads, the flow pipe is piping hot but not getting through the rads.
This might sound a bit vague but does it sound like a balancing issue or a pipe size issue or something else?
I have left them a couple of small heaters as I didnt have time to investigate fully tonight but hoping to get back saturday.