Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Frozen condensate pipe prevention in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.
Messages
43
Now that the cold weather has passed it's time to sort out what I do to prevent a repeat of the frozen condensate pipe next year.

I have a newly installed Worcester combi boiler. The condensate pipe drains into an external soil stack (1960s property). External condensate pipe about metre long with a generous fall.

How can I prevent a repeat in future years.

The Worcester CondenseSure Condensate Siphon seems to be a possible solution.

Does anyone have experience of these?

Are there other ways?

Views please.

Many thanks.
 
Any pics of the insulation atm ?
 
40mm waste pipe insulated with trace heating you can switch on at minus temps
 
Now that the cold weather has passed it's time to sort out what I do to prevent a repeat of the frozen condensate pipe next year.

I have a newly installed Worcester combi boiler. The condensate pipe drains into an external soil stack (1960s property). External condensate pipe about metre long with a generous fall.

How can I prevent a repeat in future years.

The Worcester CondenseSure Condensate Siphon seems to be a possible solution.

Does anyone have experience of these?

Are there other ways?

Views please.

Many thanks.

What size is current pipe?
 
its very good but needs a flow pipe to fix onto
 
Any chance of running the condensate internally to a waste outlet? Problem solved if you can.
 
3 realistic choices but let's look at why first.

Condensate pipes freeze because the sensible heat contained in a few drops of water are lost in an instant. There simply isn't the volume to hold much heat. The advice (originally by Corgi) to install a larger dia pipe for it to discharge into actually made things worse because the larger dia pipes encourage their own circulatory air currents making the sensible heat loss faster.

Insulation of a smaller pipe simply increases the time taken to lose heat. However even with the best of insulation, as we are talking such tiny amounts, a 50% improvement still amounts to naff all.

To stop it you have three realistic options:
1 - redirect it inside the house
2 - fit a condensate pump so that the discharge contains far more water (heat mass) so will not freeze so readily.
3 - Fit trace heating. This is the ONLY guaranteed way because it replaces the sensible heat lost by injecting replacement heat keeping the water liquid.
 
Status
Not open for further replies.

Similar plumbing topics

It’s ok aslong as the internal trap is the...
Replies
2
Views
1K
  • Locked
I’ve been in garden for three hours thawing...