AFAIK the boiler is set to fully pumped. (The switch inside is on fully pumped), however the pump is only running while the boiler burner is actually lit.

My understanding is that a fully pumped system should have the pump running for a while after the burner goes off to circulate the heated water around.

Looking at the boiler diagrams, there is a pump over run thermostat that is used when set for fully pumped, which keeps the pump running until the heat exchanger temp drops below 80c.

This stat is fed from a terminal marked Switched Live. On this installation, the Switched Live terminal goes up to the main terminal box but is not connected to anything! I assume it's supposed to go to a room stat or something?

The manual says to connect it to permenant live if there is no 'external control' fitted.

Is there any reason why this would not have been wired up? Should the pump actually run for a period after the burner shuts off?

The rads take a while to warm up and if the HW or UFH circuits are off, they take forever to warm up. I am thinking that this is because the pump isn't over running.
BOILER cicuit.jpg
BOILER cicuit.jpg
BOILER cicuit.jpg
 

Similar plumbing topics

Very informative...........thx🙄
Replies
3
Views
646
Are you controlling the stove flow temperature...
Replies
6
Views
1K
Just happened to be rummaging around on the...
Replies
10
Views
3K
Hi, thanks for the reply, that did cross my...
Replies
2
Views
875
    • Like
Great summary and well done for getting it...
Replies
1
Views
2K
Back
Top