Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Gas Appliance tube size in the Gas Engineers Forum area at Plumbers Forums

Messages
2
Good afternoon. I got a new Mapress gas installation in my catering business. All end points are 1/2" the main tubing is 32mm.
Some appliances have 3/4" hoses connected by previous owners /installers, although their inner tubing is 1/2" too - including the 6 burner/ 1 oven range cooker.
Does the use of these 3/4" hoses makes any sense? Or would you fit 1/2" all around?
From my logic I would install 1/2" on all -
 
We do commercial kitchens though mostly bigger than yours,
Everything should be sized for rating of the appliances your using that includes hoses.
Out of interest what interlock system have you fitted? We use S@S Northern much more reliable by not using air pressure switches.
 
As above all depends on the kw /m3/h load on each appliance
 
We do commercial kitchens though mostly bigger than yours,
Everything should be sized for rating of the appliances your using that includes hoses.
Out of interest what interlock system have you fitted? We use S@S Northern much more reliable by not using air pressure switches.
First thank you for your fast response.
We use our own custom build current sensing interlock system with integrated single and 3 phase speed controller, which also integrates our fire alarm system.
The valve opens after reaching a specific airflow in both systems (extraction and ventilation), can be interrupted using an emergency button in the kitchen, but also shuts down the fans in case the fire alarm goes off
 

Similar plumbing topics

  • Question
Many thanks for the reply @Timmy D thats a...
Replies
5
Views
902
Also, they could even supply their own tube...
Replies
19
Views
2K
I have connected the secondary pump to a wifi...
Replies
9
Views
2K
H
Hi there, thanks for your time to look at this...
Replies
0
Views
855
HRP123
H
Honestly, I didnt even think about that. I...
Replies
2
Views
1K
Back
Top