Can't find the info on this to hand, got to price a gas carcass for a commercial kitchen including the existing 28 kW boiler upstairs.

20kW load in the kitchen apparently so that's 4.46m3/hr I believe, what will and R5 take?
 
Can't find the info on this to hand, got to price a gas carcass for a commercial kitchen including the existing 28 kW boiler upstairs.

20kW load in the kitchen apparently so that's 4.46m3/hr I believe, what will and R5 take?
6m3/ hr pal
 
R5 just means the meter is an imperial pulse enabled and is used on lots of sizes of meter.
Under the digits it will tell you the capacity of the meter in cuft.
212cuft/h is a U6 which will be enough for the load.
 
Hang on. How did you get over 4m3 of gas for 20kw
 