On a Primary/Secondary meter system you only have about 20-25mb in the main riser, not 75mb.
The 75mb - 2 bar pressure is usually a gas meter governor inlet service side pressure, for individually mains connected meters. But that would be at the inlet to the Primary meter not the Secondary meters, they are just really governor less flow meters.
If you use Secondary meters on domestic, you usually have to treat the whole place like one big house and work out sizes as though its one house, so that each appliance in every flat gets a minimum of 20mbar with everything in the block of flats working flat out.
Okay so you can drop 1mbar, but that is only an allowable drop not a standard.
It works a bit like:
If you can only suck so hard up a straw, and you only get 1 pint of water in a minute up the straw, but you want more than a pint in a minute, you get a wider straw.
In this case increase the flow.
So to work it all out, you need a load of figures, resistances and route descriptions which basically, we haven't got.
If however your on governed down individual supplies with 20-25mb at the outlet and your boiler position is only a few feet away from the meter. Then you should be okay with 22mm or even 15mm to the boiler. Must admit I prefer it in 22mm and reduce down close to the boiler.