Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Gas pipe extension 15mm or 22mm (from a 28mm supply). in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.
L

Len

Posted this last week in the wrong forum so this is a (modified) repeat and I like to three who answered that post.

Currently have a very old open system gas boiler which services the hot water system, via a storage cylinder and a ring of 11 radiators.

Needs to be replaced and I have selected the plumber to carry out the work. Others who quoted for the work mentioned that the gas feed would have to be upgraded to 22mm (based upon the visual inspection of 1.6m of 15mm pipe rising from the floor to the current boiler). Only one asked about the current pipe work feeding to this 15mm length.

The proposed condensing boiler to be installed is the Vaillant Ecoplus 618 which has an inlet gas pressure requirement of 20mbar on a 15mm connection.

The position of the new boiler is up in the loft which will require a 6mtr extension to the current gas pipe.

The feed from the street to the gas meter is 28mm steel reducing to 22mm copper and the outlet from the meter is 22mm copper back to 28mm steel that then goes under the floor (solid) across to the garage and then is fed up to a T in the floor - a length of 4.3m. The T splits the gas to the 15mm for the boiler and then goes under the floorboards to feed a supply to the cooker which is not used.

Unfortunately the split happens under the dining room floor which is covered in wood laminate. To access the joint will require the room to be cleared and the whole floor being lifted.

My neighbour had his boiler moved to the loft about 2 years ago and the installer used 15mm pipe all the way.

Have read numerous feeds about 15mm vs. 22mm and the Corgi changes to the regulations and have got confused..

I do not know the gas pressure into the house – but surely the size of the gas inlet pipe should be enough to feed the required mbar pressure required by the boiler?

Thank you any guidance you can offer.

Regards
 
try simplify to the following.
and will work it out for you,
size of meter first
appliances been supplied in k/w
size of pipe to first tee etc
size and length of pipe to first appliance +k/w requirement
size and length of pipe to remaining appliance. k/w requirement
 
Thank you for your reply and offer to help here are the answers to your questions:

size of meter - unknown but Manu. is Actaris (M32 Epsilon) installed Jan 2006 [govenor states Inlet 30m/Outlet unreadable Type 1&2 500 ft 3"(?) Maxflow stamped in the metal]
appliances been supplied in k/w - only 1 at 18kw
size of pipe to first tee - 28mm [length 4.3m]
size and length of pipe to first appliance - 15mm [length 9m] – 18kw (moving boiler to loft - extending pipework by 6m)
size and length of pipe to remaining appliance. - 28mm [length 5m] – Cooker point [not used].


Will look at the meter again if you can help with suggestions of what to look for.

Regards
 
9 meters of 15mm copper feeding 18kw will be undersized.
 
Thank you for your reply and offer to help here are the answers to your questions:

size of meter - unknown but Manu. is Actaris (M32 Epsilon) installed Jan 2006 [govenor states Inlet 30m/Outlet unreadable Type 1&2 500 ft 3"(?) Maxflow stamped in the metal]
assume its a u6/ga capable of supplying 6 cbm per hour

appliances been supplied in k/w - only 1 at 18kw
size of pipe to first tee - 28mm [length 4.3m]
size and length of pipe to first appliance - 15mm [length 9m] – 18kw (moving boiler to loft - extending pipework by 6m)

15mm not big enough require 22mm should do

size and length of pipe to remaining appliance. - 28mm [length 5m] – Cooker point [not used].
 
Status
Not open for further replies.

Similar plumbing topics

Thank you for the replies. I had another...
Replies
4
Views
835
Di do not know much about this heating stuff...
Replies
16
Views
2K
More than fine then in 11/5 tube should be...
Replies
3
Views
629
A bit late but what were the test results, did...
Replies
10
Views
3K
Thanks for the reply. I am going to get a...
Replies
14
Views
3K
Back
Top