I need to add a cooker supply and have been trying to work out the sizing of the pipe but have come unstuck as can't see anything over 30 meters in 'THE' chart. Have checked Corgi, Viper and old text books with no luck.
All lengths include allowance for pipe and fittings (copper).
A-B = 7.5 Meters
B-C = 5 Meters
B-D = 28.5 Meters
B = TEE
C = BOILER @ 2.6 m3/h
D = COOKER @ 1.04 m3/h
Using the chart, so far, A-B needs to be 28mm, B-C needs to be 22mm but as the theoretical pressure loss over the B-D is 0.33mbar I haven't a clue what to do as multiplying it by 3 gives 85.5 Meters which there isn't an option for.
What can I reference?
Does anyone know? Other than saying ''just use 28mm for a few extra meters son''.
Thanks