Situation:- Service to Worcester Greenstar 28i Junior.
All good as far as CO2% (9.8 Max 9.2 Min), condense trap cleaned, flue and terminal good ect, ect.
Then when i do the gas rate to start with i only got 20.95kw (nett), i need 28.57kw.
OK, i check standing pressure at meter (23.5mbar) then check working pressure (20mbar) and then pressure at appliance (19mbar), so all good on that front.
Check gas rate again and get 26.77kw nett, still not enough. Check again and again and still get 26.77kw. So i check the pipe sizing, 8.5 meter pipe run with 16 (yes 16) elbows, so this makes equivalent of 16.5 meter pipe run (22mm), this is still OK and should give me enough gas.
Cant get through to worcester at the moment. Anyone any idea what might be wrong?