Hi all,
I am new to this forum and I must say straight away that I am neither a plumber or a gas engineer, just a confused citizen seeking your help.
I have a gas central heating boiler that is about 35 years old and I would like to work out how efficient it is.
I have used the formulas given on this and other forums but I am still confused by the results I am getting.
I am setting my boiler to run full pelt then timing how long it takes for the dial on the gas meter to do one revolution. I have included a picture of my meter.
The dial is taking 132 seconds per revolution ( checked several times ).
From all the formulas that I have used it returns an answer of about 8KW.
My boiler is an Ideal Concord WRS255. Heat I/P, min 17.9KW, max 21.4KW.
Heat O/P, min 13.2KW, max 16.1KW. These figures are from off the boiler door itself.
Here is my confusion how is it that I am getting an answer of 8KW when the boiler states Heat I/P max as 21.4KW.
Hope some kind sole can enlighten me.
Thanks.
I am new to this forum and I must say straight away that I am neither a plumber or a gas engineer, just a confused citizen seeking your help.
I have a gas central heating boiler that is about 35 years old and I would like to work out how efficient it is.
I have used the formulas given on this and other forums but I am still confused by the results I am getting.
I am setting my boiler to run full pelt then timing how long it takes for the dial on the gas meter to do one revolution. I have included a picture of my meter.
The dial is taking 132 seconds per revolution ( checked several times ).
From all the formulas that I have used it returns an answer of about 8KW.
My boiler is an Ideal Concord WRS255. Heat I/P, min 17.9KW, max 21.4KW.
Heat O/P, min 13.2KW, max 16.1KW. These figures are from off the boiler door itself.
Here is my confusion how is it that I am getting an answer of 8KW when the boiler states Heat I/P max as 21.4KW.
Hope some kind sole can enlighten me.
Thanks.