Simple, this is part of the engineers experience, and heres a new one for you. 1st you must do a G20 inlet operating pressure to ensure the gas has been sufficiently regulated down. You may know this as inlet working pressure. you are ideally looking for the appliance if nat gas design pressure of 20mb, but since the meter regulator is allowed +/- 2mb from 21. min 18. However check the manufacturers manual, if forced draught may accept 17mb inlet (ie a vaillant). You can't gas rate and so you must do a flue gas, this will confirm the air/gas mix is correct and complete combustion is there. Stripping it down you also show you if there is any blockage or dirt in the air and flueways inside the appliance and look for soot or scale on the heat exchange which may suggest a lean or rich mix. That way you are visibly confirming your flue gas readings. Ensure you work only on the appliance. Any work on the supply will not be permitted without a Commercial Licence. You should be able to test for tightness so long as an AECV is fitted in the property, using the G20 inlet test point again. remember no meter means permissable drop of 8mb on existing installation so long as pipework does not exceed 28mm. NOTE: ADVISE ONLY: I am not there so refer to your Manufacturers manual or get download it before going !! Keep your BS Book with you for reference too. Good luck, but if in doubt shout, or pass this one over to the commercial boys. (Remember - Advise Only)