Gas rating.?????? | Gas Engineers Forum | Plumbers Forums

Welcome to the forum. Although you can post in any forum, the USA forum is here in case of local regs or laws

Discuss Gas rating.?????? in the Gas Engineers Forum area at Plumbers Forums

Status
Not open for further replies.

Hobo128

Gas Engineer
Messages
292
Gas rating a greenstar 30si. Put in service mode-2min test meter index 0.095. 0.095x3600x10.76/120 =30.666kw
In the technical data this matches what it says for maximum rated heat output dhw.
If you covert 30.666kw to m3/h 30.666x0.095 = 2.91327m3/h. In the technical data it says it should be 3.24m3/hr
Tb141 says it can be 10% below MI so 3.24 x 0.1 = 0.324 (10% of 3.24) 3.24-0.324 = 2.916
So the absolute minimum it can be is 2.916m3/h and im getting 2.91327m3/hr. Am I ok ?????
 
I make 30.66 kw 3.14 m3/h Even by your figures tho its so little I wouldn't worry about it, if you are adjust the air gas ratio valve a bit as its prob not bang on.
 
???? why times it by 3600 and divide by 120?

we just learnt x 30= m3/hr x 10.77 = kw.
 