Hi all. Hope you are all good and are doing ok with work due to lockdown, self isolating etc.

What instruments did people purchase to comply with this bulletin?

I only paid £160 for a fluke 116 last year and now need to spend a lot more due to this bulletin.

Cheers all.
 
remove fuse spur
prove multi meter
multi meter case to check its not live

done
 
Multimeters aren’t recommended to dead test for safe isolation anymore. It should be a test lamp or two pole voltage tester to GS38.

I don’t see why not there an approved electrical test device

think it’s another one of those people don’t know how to use them properly so they have kept it simple
 
think it’s another one of those people don’t know how to use them properly so they have kept it simple
I’ve just read the document from hse (4th edition) which appears to have changed to possibly include multimeters? I distinctly remember it stating they shouldn’t be used, as the incorrect selection of range could be used, eg Vdc instead of Vac. It does however state must meet certain criteria. Maybe they changed it as people didn’t want to shell out on new equipment?
 
I’ve just read the document from hse (4th edition) which appears to have changed to possibly include multimeters? I distinctly remember it stating they shouldn’t be used, as the incorrect selection of range could be used, eg Vdc instead of Vac. It does however state must meet certain criteria. Maybe they changed it as people didn’t want to shell out on new equipment?
Didn’t want to shell out when there was no need to. Learn how to use a multi meter correctly. That’s where they should be focusing.
 
I’ve just read the document from hse (4th edition) which appears to have changed to possibly include multimeters? I distinctly remember it stating they shouldn’t be used, as the incorrect selection of range could be used, eg Vdc instead of Vac. It does however state must meet certain criteria. Maybe they changed it as people didn’t want to shell out on new equipment?

You got a link to this mate?

All I can find is what you were saying...

Proving electrically dead
Once the means of isolation has been identified and following the isolation of the equipment, it is vitally important the equipment is checked to ensure it is electrically dead before work commences. The use of an approved voltage indicator is required to prove that the equipment is dead; this could be a proprietary test lamp, or a two-pole voltage detector. The HSE recommends that a multi-meter is not used for proving dead (HSG85(2)).
 
https://www.hse.gov.uk/pubns/priced/gs38.pdf I couldn’t seem to find information regarding not using a multimeter to prove dead, only single pole voltage or non contact voltage indicators. That said, I haven’t read it thoroughly and may have missed it.
Pretty much says what is said above in previous post about people selecting the wrong range with a multimeter so they should not be used. Hmmmm
 

Similar plumbing topics

Ahhh that one it’s a nope from me failed...
Replies
4
Views
721
Just browsing the threads and this one here //...
Replies
0
Views
1K
Set whatever boiler you're installing to the...
Replies
2
Views
917
My approach to everyone is that there looks to...
Replies
8
Views
2K
I am about to start a training course to...
Replies
0
Views
1K
Back
Top