New pipework you are not allowed no drop (tolerance) existing pipe work you are allowed 4mb over 2 mins( providing diameter of pipe work does not excede 0.35 then you would have to test as up1a not 1b) not 0.4 providing their is no smell reported based on a u 6 metre, the e series meters you are allowed 8 mb .Thus if you did install a section of new pipe work it would be prudent to treat the whole installation as new pipe work and no leakage allowances allowed ,if it was a commercial installation you could splay off new section and hydraulic test or pressurised with air or nitrogen but you would not do this on a domestic senerio because you are only dealing with small volumes. yes you are right allowances were given to equipment connected to gas train.cookers rely on gas cock grease taper jet spring and knitting plate to seal gas tap into female housing ,you can get passing through multi functional valves when you turn boiler off to do a soundness test AR untill you no better, gas fire valves can pass, gas never no smell because it drawn up through the chimney. worst senerio very common some dick head installed compression fitting under floor boards and it is weepping ,or very old installations were they have used fairy liquid as a leak detector corrosion in evidence so and so on ! So to realiterate you are allowed 4mb permmisable leakage rate over 2 mins not 0.4 providing let by test ok ! and if you extended existing pipework with new treat the whole installation as a new install and no permmisable leak rate allowed hope this may help