Had to go and look at a boiler last week due to a smell of gas, got there and found they are smelling it outside from the flue. So instantly thing the gas valve, close the valve at the boiler, stick the gauge on the inlet pressure test point on the valve and sure enough its dropping. Cap boiler off and call vaillant as the boiler is only a year old and under warranty. Get a call from the vaillant engineer today saying there is nothing wrong, only to find out he is testing it for a drop with the gas turned off at the meter and not the boiler and saying he wont replace the gas valve as it isnt dropping that much. It took me about 5 mins to convince him it is 100% at fault.