Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Glow Worm Compact 100E in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

fubar1000

Gas Engineer
Messages
199
Afternoon all

I fitted a gas valve in the above over a week ago & now the boiler is doing the same thing again

Boiler would light for around 3 sec then go out, this would continue until the boiler was manual shut down.

Fitted the new gas valve, tested & the boiler run like a dream.

Now the custard has just phoned to say the boiler runs for 3 sec then goes out

A/P/S seems ok, fan seems ok, no other issues with the boiler

Any ideas please people????
 
Check to see if dhw light is slightly lit, if so the gland on the dhw valve is leaking onto & shorting the micro switch & causing the boiler to fire up. Can also cause it to overheat or just fire up for short intervals, thinking it's diong dhw.
 
aggis is the winner lol

The dhw light advice was spot on

How on earth would I'd find that without the little nod from aggis I don't no

Big thanks for that mate

Merry chrimbo people
 
Check to see if dhw light is slightly lit, if so the gland on the dhw valve is leaking onto & shorting the micro switch & causing the boiler to fire up. Can also cause it to overheat or just fire up for short intervals, thinking it's diong dhw.

That's one for the little black book
 
I had one where another engineer had fitted gas valve and not set min burner pressure so when it modulated down it went out . worked fine on hw and heating until temp reached .pcb poor on these boilers
 
Status
Not open for further replies.

Similar plumbing topics

I once had a similar experience with my old...
Replies
6
Views
856
Thank you for the advice I've sort it out it...
Replies
3
Views
677
A decent water pressure and flow will be...
Replies
4
Views
1K
You could try jet flushing it with x400 or...
Replies
9
Views
204
Open all the windows and doors to loose the heat.
Replies
7
Views
2K
Back
Top