glowworm ultimate 100 ff

Status
Not open for further replies.
A

andf380

Boiler not firing up on demand there is 1 neon light on went through the checks to test if there was 240v and ok tested the fan and there was a ohms resistance of 65 ohms turned on the demand and checked if there was 240v at the fan and it was 0 checked back at the board and it was 0 on the board did a beep test on the harness and the harness was ok i am assuming the board needs replacing Would appreciate any advice
 
i have checked the manual overheat stat but not checked the temperature stat
 
Have you checked the fuse(s) on the PCB, if I remember rightly there are 2 different boards available for the Ultimate FF, one has a single fuse while the other has 2 fuses. Also check that the air pressure switch is not stuck open as I have known it to do so a couple of times, when it does it will not start the ignition sequence. hope this helps,
Martin.
 
Thanks Martin will call tomorrow and check the fuses and the air pressure switch
Thanks
Andy
 