Had a call early today to a Grant 36e internal combi.
Fault was no heating but had hot water.
Turns out various engineers had visited and the customer has lost faith.
Forts thing I noticed was an array of parts strewn across the floor, solenoid, oil pump, pressure switch, 2 air vents and a flow switch which had been nibbled around the paddle which the customer said that’s what engineers do when it don’t work!!!!
So the system doesn’t have enough expansion so I’ll return and sort that.
the boiler was staying in hot water demand with flow and I tested and found out the flow switch was broken and also not installed the correct orientation.
Having changed that the boiler heated up the tank but took about 20 min after the burner stopped to switch to CH. After 2 to 3 minutes of firing with the CH on it switches back to hot water again and this happened all the time I was there. The boiler doesn’t always fire when it goes back to HW and the flow light on the panel is never on only if you open a tap. Therefore the heating never stays in long enough to heat properly.
So is the fault a faulty HW (white) thermistor or the phial it goes into on the slave tank scaled up possibly?
Would appreciate anybody’s experience if you have had this issue and possible remedy please?
Regards 👍
Fault was no heating but had hot water.
Turns out various engineers had visited and the customer has lost faith.
Forts thing I noticed was an array of parts strewn across the floor, solenoid, oil pump, pressure switch, 2 air vents and a flow switch which had been nibbled around the paddle which the customer said that’s what engineers do when it don’t work!!!!
So the system doesn’t have enough expansion so I’ll return and sort that.
the boiler was staying in hot water demand with flow and I tested and found out the flow switch was broken and also not installed the correct orientation.
Having changed that the boiler heated up the tank but took about 20 min after the burner stopped to switch to CH. After 2 to 3 minutes of firing with the CH on it switches back to hot water again and this happened all the time I was there. The boiler doesn’t always fire when it goes back to HW and the flow light on the panel is never on only if you open a tap. Therefore the heating never stays in long enough to heat properly.
So is the fault a faulty HW (white) thermistor or the phial it goes into on the slave tank scaled up possibly?
Would appreciate anybody’s experience if you have had this issue and possible remedy please?
Regards 👍