Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Grant 50/90 Riello RDB not working in the Gaining Plumbing Experience area at Plumbers Forums

M

MJPH

I have a problem with my Grant 50/90 oil boiler and Riello RDB burner.( located in garden in cabin pac ) Nothing is happening at the boiler !! The timeclock is on, the pump is running, 0.5 - 1.0 bar system pressure, room stat calling for heat and motorised valve open for heating. Boiler is not locked out, overheat stat has not tripped out but nothing happening ? Any ideas ?
 
No frost stat fitted but I was wondering if it could be the actual boiler stat ? Would this always lock out if there was a fault or could it just stop calling for heat ??
 
If the burner has locked out there will be a light on the lockout button on burner. If this is not the case there may be a fault in the thermostats. It is possible to have a faulty control box on burner, that shows no red light, but this is rare. Have the power to burner checked first.
 
No frost stat fitted but I was wondering if it could be the actual boiler stat ? Would this always lock out if there was a fault or could it just stop calling for heat ??
The main, control stat if failed, would let the boiler overheat & then the limit stat would limit the temp by turning off permanately. It is only resettable manually by the limit reset button. ( some limit stats are automatic types, that reset when temp lowers, but normally not)
 
Hi Gray0689 Please see from original post : Nothing is happening at the boiler !! The timeclock is on, the pump is running, 0.5 - 1.0 bar system pressure, room stat calling for heat and motorised valve open for heating. Boiler is not locked out, overheat stat has not tripped out but nothing happening ? I think it must be a control issue as it seems like the boiler is not being called for heat !!!
 
Can you hear a slight humming or buzzing noise from the boiler, check to see if you have a live supply to the burner.Something may have seized such as the pump or motor or even the capacitor might not be generating enough power to start the motor, this is usually accompanied by a buzzing noise.
 
As the water pump is running, the burner should be getting power. Check limit stat as has been said by a lot of us, & if power is getting to burner, then control box is likely if no lockout.
 

Similar plumbing topics

If the boiler is connected to a conventional...
Replies
1
Views
571
All sorted now and running better than ever...
Replies
3
Views
1K
Wait until you can get hold of somebody with...
Replies
4
Views
926
Hi. I've taken a break from all the sites I...
Replies
8
Views
3K
Thanks everybody for your advise. Will call...
Replies
8
Views
5K
Back
Top