hi got an install to do 'exsisting, ground floor boiler ,loft (2nd floor) cylinder-FE tank, 28mm flow return to boiler reducing to 22mm onto cylinder coil with the OV and WF from FE tank on 22mm flow just before cylinder. heating pumped ground floor 22mm reduced to 15mm - typical 70-80's set up would like to convert fully pumped but cant figure how with out ensuring system vented at all times. pipes in solid floors down stairs so dont want to pressurise?
can i still put a new boiler onto this system if i 2 port the Gravity return and fit cylinder stat (C plan) ?????
prob used to be a common prob any ideas greatly appreciated
cheers illloyd