Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Gravity fed hw system in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

zeebeedee

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,143
I have little experience on these old systems. A mates bought a house with the setup shown. Had a quick look today, heating on boiler and pump fires rads heat up. Hw only pump goes off boiler cycles, flow gets red hot returns cold. Any ideas?
image.jpg
 

Attachments

  • image.jpg
    image.jpg
    68.3 KB · Views: 26
  • image.jpg
    image.jpg
    74.8 KB · Views: 20
The hw tank is directly above the boiler. Is this normal for gravity hw set up?
 
Pumped heating gravity hot water, I've only ever seen gravity hot water with 28mm pipe work though.
 
Yes Normal for grav. But don't think that boiler is designed for grav hw. It should be a fully pumped system i would just bosh in a two port and a bypass - gate vale
 
Yep I can see that now, teach me to take a quick look and start flapping my gums :90:
 
Yes Normal for grav. But don't think that boiler is designed for grav hw. It should be a fully pumped system i would just bosh in a two port and a bypass - gate vale

Thats what I suggested would be easy enough 2 port on the flow to the heating circuit.

Will be be done in the near future he's having the damp sorted first and kitchen/bathroom done. In the meantime any ideas on how to stop the boiler cycling for now?
 
When you say having damp sorted not got the injection cowboys in has he? The solution is not injection it's ventilation.
 
When you say having damp sorted not got the injection cowboys in has he? The solution is not injection it's ventilation.

No a builder mate of ours is doing it, cowboys where in previously "injecting" for the previous owner. One of the lads has striped it back to the brick and. It's getting tanked Monday whatever that means
 
No move pump so it's fully pumped . I.e right off top of the boiler then tee up for DHW and down and add in a two port or put in a 3 port instead I a tee.
 
It should have been converted to fully pumped when that boiler was installed. Shocking that it was not.
 
It should have been converted to fully pumped when that boiler was installed. Shocking that it was not.

A property management place I look after with a BBU has the same set up..... Horrible, ancient old things :(
 
Bbu love grav DHW. As long as injector elbow and separate conn for rads on opposite side as injector and primary's on same side.
 
What is the difference between a boiler that will operate on gravity fed hw and one that wont? Ive seen switches on some older models that will do both. Hows does it alter the operation of the boiler?
 
Bbu love grav DHW. As long as injector elbow and separate conn for rads on opposite side as injector and primary's on same side.

The cylinder bubbles away nicely when the stat gets set about 2 though :lol:
 
What is the difference between a boiler that will operate on gravity fed hw and one that wont? Ive seen switches on some older models that will do both. Hows does it alter the operation of the boiler?

I'm sure iron hex and setting on grav means lower burn . As convection wicks the heat away. Plus block needs to promote grav circulation.
 
Status
Not open for further replies.

Similar plumbing topics

Everything working fine on PP mode - thanks...
Replies
7
Views
914
  • Question
Many thanks John I had already bought two...
Replies
2
Views
914
Very informative...........thx🙄
Replies
3
Views
572
Hello, I live in a two floor semi with a...
Replies
0
Views
764
I don’t know your boiler but would expect it...
Replies
3
Views
669
Back
Top