Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss gravity flow back boiler in the Boilers area at Plumbers Forums

Status
Not open for further replies.
Messages
4
I'm hoping to have a back boiler woodburner installed, which can work to heat cylinder by gravity even when no power (still happens!). Looking at other threads, I fear that pumps MUST now be installed, so is this not now allowed?
 
Older heating systems with hot water by gravity circulation and pumped central heating are no longer considered efficient. However, design for back boiler off woodburner would need to circulate by gravity in event of pump failure.Position of DHW cylinder,size of flow and return pipework, heat resistant F&E tank, heat sink.are all necessary considerations.Properly designed the system should work with no power to the pump. ( or even with pump removed).
 
What type of cylinder are you thinking of, not un-vented I hope ?

What are you going to use to heat the hot water in the summer ?

As above, a thermal store can be a good option.
 
I currently have a small uninsulated copper tank, fed from cold tank in loft, with expansion/overflow up into cold tank. Advice from local man was I need a mains pressure hot cylinder, with pressure release valve to outside- is this what is called Unvented? (mains Cold pressure is adequate). Thanks.
 
Don't mix unvented cylinder and solid fuel boiler. A thermal store is a different animal which delivers hot water at mains pressure, like an unvented cylinder, but is compatible with solid fuel if correctly positioned.
 
Status
Not open for further replies.

Similar plumbing topics

Very informative...........thx🙄
Replies
3
Views
572
200% won’t be the reason the cylinder isn’t...
Replies
10
Views
1K
S
Boiler Fault I’m hoping someone can help with...
Replies
0
Views
114
S
Sounds like you have found a blockage, if so...
Replies
6
Views
1K
RobinA
R
Back
Top