Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Greenstar 24i Junior (LPG) problem in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

myles

Gas Engineer
Messages
81
Evening all,

Has anyone came across an issue where the boiler will light then 2-3 seconds later goes out sounds like its being snuffed out not like when no flame rectification, I have checked everything I can think of relating to the gas/air mix. Changed the gas/air mix manifold at back of fan as the flaps were stiff, tried resetting gas valve, changed rubber gas pipe as it was looking a bit iffy (cracking) cleaned main heat ex and flushed condensate through new gasket and electrode set, flue is clear as far as I can tell (vertical flue) good pressures at valve too. British gas were looking after it before the place went into administration and this boiler has had a new fan and plate hex recently however it wasn't working when I arrived and gas was isolated so guessing it is an ongoing problem! Spoke with Worcester tech and basically I have tried everything they had said even put another gas valve on just in case that was the problem but no difference! Fault finding chart has not been much help either. error code is slow flash normally off with reset light on which correlates to ignition fault which I ran through the list to no avail. This has been a head scratcher today to be honest! :89:

Any help would be much appreciated!

Thanks

Myles
 
Bottles or tank? You say good pressures have you checked with two gauges ( one at chb other at ISO on incoming? Had a fire on bottles, that the changeover was goosed.
 
Sorry should have said lol its tank fed, no problems pressure wise unfortunately!
 
what pressure you got incoming to boiler?
 
As far as I can see it is all clear, might have to get my inspection camera in there lol
 
As far as I can see it is all clear, might have to get my inspection camera in there lol

yea since you have gas supply (and new gas valve) new spark as well

did you try lighting with front off aswell?
 
Yep, if it's not the flue then God knows as I have checked everything! Three properties there and so many issues with the installs from non gas isolation valves, hotplate mounted onto combustible workspace with scorch marks, split cooker hoses, 20+ meter long condensate runs the list goes on!
 
Yep, if it's not the flue then God knows as I have checked everything! Three properties there and so many issues with the installs from non gas isolation valves, hotplate mounted onto combustible workspace with scorch marks, split cooker hoses, 20+ meter long condensate runs the list goes on!

if its not the flue, it might be easier in the long run to get Worcester techs out to fix it least they will have any parts on the van/near by
 
if its not the flue, it might be easier in the long run to get Worcester techs out to fix it least they will have any parts on the van/near by

ive had a couple like this on natural gas where it will light green light on for a few seconds and then go out....I did everything you did, changed electrodes, cleaned heat ex, checked leads for continuity, checked pressures.....one guy before me changed fan....in the end cos I couldn't think what else to do so I replaced the pcb and it worked fine. Since then I have had the same problem twice and found if I changed electrodes and pcb it was ok.
 
Daft question buddy what colour is the data plate? Is the code plug lanyard still attached? What fan depression are you getting on the white test point on the banana? Oh and does the ionisation led light at all.
 
Moogwai next time try disconnecting and reconnecting the main low voltage plug from the board a few times. Sometimes is a bit of tarnish on the pins.
 
I tried everything mate, disconnecting, re-plugging.....had the pcb out a few times to check for scorch marks and dry joints!!! stupid things them worcesters.....never liked the junior range!! lol
 
This one has the yellow data badge, I'm back there in the morning and will be sticking camera in flue to check it, had to wait for return of my analyser as the screen got cracked! Love lanes service though posted tues afternoon back today at 9:30! The light did illuminate when it ran for a few seconds. Checked with a spare pcb I had on van that I know works still same issue and code plug firmly connected too! Bloody Worcester juniors!
 
stick your analyser in the air test point, if you get high Co2 the flue seal is knackered. Or you have an internal disconnection.
 
Status
Not open for further replies.

Similar plumbing topics

If you have the right temperature rise for the...
Replies
10
Views
3K
There is 6 pipes under the boiler and one goes...
Replies
19
Views
971
Hello All- (Usual caveats apply: I am the...
Replies
0
Views
172
hose not perished they split very easily and...
Replies
7
Views
2K
Just for completion, and to have this archived...
Replies
8
Views
2K
Back
Top