Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Greenstar 28 I junior ignition lockout in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

flesi

Gas Engineer
Messages
93
Hi guys , having an issue with the "great" greenstar . Basically it does try to fire up, u can hear the spark clicking , it does try few times then it goes to lockout.(flushing lights) Checked the gas valve , condensing trap , can't check the ratio .before I start striping out .. any suggestion ? Cheers
 
Is it passing any gas? Inlet filter could be blocked with black dust

i carry a spare set of electrodes to check the leads if they are ok.

what readings did you get for the solenoids?
 
Does gas pressure drop slightly when it try's to ignite ? The fan is running right??
 
I did suspect the fan, it's seems running ok but when boiler does lockout it runs for few second on higher speed than it stops
 
If its sparking, you need to confirm its getting gas.
 
Need to go back to it and strip it down and have a full check, need to get better with those worcesters as I got the same boiler on my own house ( not installed by me by the way)
 
After striping the boiler out , cleaned the baffles , changed the electrode and the seal...... Still the same issue , boiler won't fire up. Tenants on my head. Checked everything again gas valve 35 dc, resistance on coils ok, fan running ok , inlet pressure 21 mbar. I ran out of ideas until I checked the meter ... Guess what I found???
 
Does inlet pressure drop a tad when it tries to light? If not could be gas valve.
 
Restriction at meter? half shut ECV? meter swapped for bicycle inner tube?!
 
Yep ECV half shut after the lovely tenants threw all the shoes on it and turned the ECV half way down. So I was getting 21 mbar inlet standing pressure but the boiler start firing up the pressure would go as low as 6 mbar . I thought it was the regulator on the meter.
 
Status
Not open for further replies.

Similar plumbing topics

So it’s definitely more reliable when the hot...
Replies
4
Views
1K
Can I have your gas reg number please so I can...
Replies
1
Views
676
End to end test it would be my next port then...
Replies
3
Views
1K
Thanks some good ideas. Just as an aside if we...
Replies
10
Views
2K
Need a gas safe engineer out if you’ve been...
Replies
8
Views
2K
Back
Top