GrahamM

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,044
Attended the above 5 year old boiler for annual service.
Cleaned through the magna booster and brought pressure back upto 1.5bar and left boiler on as elderly customer feeling the cold.
Went on to service fire and as I went to turn boiler off to gas rate fire, noticed pressure was up at 2.5bar.
E/V checked and again pressurised boiler to 1bar removed fill loop key and left boiler on as filled out paperwork. Pressure was soon back over the 2 bar mark within 10 mins.

Mains water entering the heating system through burst heat exchanger???
 
could well be it can happen,you need to turn the cold off to it,record the pressure reading and return to it within a few hours if its stays the same phex has failed
 
Sounds like a plate heat exchanger has pin holed to me aswel. As Gasman said, you need to isolate the cold into the boiler to test. Perhaps it could also be the flexi to the expansion vessel blocked? Not seen this on a Worcester but had it on a few vokeras before,
 
Sounds like a plate heat exchanger has pin holed to me aswel. As Gasman said, you need to isolate the cold into the boiler to test. Perhaps it could also be the flexi to the expansion vessel blocked? Not seen this on a Worcester but had it on a few vokeras before,
good call on the flexi
 
Had plates on cdi pin hole wouldnt be suprised if this is the same.
 
i had a few flexis on these boilers block up with crud last year which had the same effect a pressure rise . Annoying thing is that you have to get boiler off the wall to do something that takes 5 mins ,,,,grrrr worcesters = tat !!
 
If flexi, drain boiler, undo clip, use a long cable tie (point on end helps) to feed up and unblock, get wet, mop up black crud, replace hose and test, 10 mins job done......
 
How did you check the expansion vessel?
Remove schrader and fill system. No sign of water from valve usually indicates the vessel bladder is sound.
Put in new schrader, open drain valve and pressurise to 0.8-1 bar. Refill system. Job done......usually!
 
Could be the phex, but is the filling loop completely disconnected? If not, could be passing. If you isolate the cold to the boiler and open the hot tap, the pressure might go down, so would confirm phex fault.
 
Remove schrader and fill system. No sign of water from valve usually indicates the vessel bladder is sound.
Put in new schrader, open drain valve and pressurise to 0.8-1 bar. Refill system. Job done......usually!
Very thorough way of checking, just thought I'd ask because some don't check properly! Best way to rule out the phex, as other have stated is to isolate the the cold feed to the boiler and see if the problem persists. If it is any consolation, they are fairly easy to replace, two screws to remove and you should be able to maneuver it out from behind without disturbing anything.
 
Status
Not open for further replies.

Similar plumbing topics

If you have the right temperature rise for the...
Replies
10
Views
3K
If there’s is the chance that many things will...
Replies
10
Views
2K
Hello All- (Usual caveats apply: I am the...
Replies
0
Views
205
Thanks Chuck for the quick response I...
Replies
3
Views
1K
hose not perished they split very easily and...
Replies
7
Views
2K
Back
Top