Hey friend, we're detecting that you're an American visitor and want to thank you for coming to PlumbersTalk.net - Here is a link to the American Plumbing Forum. Though if you post in any other forum from your computer / phone it'll be marked with a little american flag so that other users can help from your neck of the woods. We hope this helps. And thanks once again.

Discuss Greenstar 30 CDI in the Plumbing Jobs | The Job-board area at Plumbers Forums

Status
Not open for further replies.

quality

Plumbers Arms member
Plumber
Gas Engineer
Messages
4,293
Hi guys I have a job to look at the above heat only boiler which keeps coming up with a EA fault code suggesting flame faliure. I went a few weeks ago and checked the gas pressure which was fine and reset it but the customer says the fault has re-occurred. it will reset and run then throw this code up when it wants to. I am no worcester expert but I`m sure one of you guys are, any ideas.Thanks in advance :wink5:
 
Hi mate

clean the electrodes and check the baring plate in the fan they stick sometimes giving a EA fault code intermittently I usually bend the ribs ever so slightly this works for me
 
Hi guys I have a job to look at the above heat only boiler which keeps coming up with a EA fault code suggesting flame faliure. I went a few weeks ago and checked the gas pressure which was fine and reset it but the customer says the fault has re-occurred. it will reset and run then throw this code up when it wants to. I am no worcester expert but I`m sure one of you guys are, any ideas.Thanks in advance :wink5:

there's a flap bit just after the fan that sometimes sticks (cant remember what its called). check co2 if it goes all over the place its that. there about a tenner.
 
Don't bend the ribs on the bearing plate, use talc as WB techs do then increase the fan over run time via the on board software from 30 secs to 1 min this happens in extremes of temp, ie, loft, garage or when a kettles under boiler etc.

if boiler is over 4 years fit new probes
 
Bearing plate probably shreaddies, - as said above replace it £10 electrodes a mess and bet front ends never been unbolted and cleaned out.
 
Status
Not open for further replies.

Similar plumbing topics

So it’s definitely more reliable when the hot...
Replies
4
Views
1K
The Sunvic arrived a few days ago but I...
Replies
18
Views
2K
DIDN'T check!! I didn't *work* on the boiler...
Replies
8
Views
141
PCB replaced. Job done. All working. Cheers.
Replies
3
Views
3K
Back
Top