I got called out today to this boiler which kept going to lockout apparently the last tenant ran out of oil the landlord had it topped up new tenants have been in for a week and the boiler wasnt working. I thought great pull some oil through fire it up and test pressures smoke fga etc.
So pulled oil through went to fire it up explosive ignition ran for 3-5 secs started to vibrate like mad so I knew it wasnt right pressure was fine and not bouncing up and down so no air and filters were clear. Next I thought it was choked up checked combustion chamber not really dirty not enough to cause that anyway.
Asked have you got the manual (Of course they didnt that would make life far too easy) and it was to late to call tech so I looked at the air setting it was set at 16 I thought to myself most worcesters are around 3-4 I will try reducing it a bit so dropped it down to 10 and tried again explosive ignition gone but it ran then went to lock out sparking constantly so I checked photocell ran constantly so photocell fine its just not set up right.
Dropped air to around 4 ran fine checked smoking quite a bit so up to 6 when it stopped smoking so checked CO2 which was at 15% they are usually around 12% so I thought I would set it up around that the closest I could get was 12.9% otherwise it would not run it still drops out every now and then about 15mins.
So at the moment it is set up
CO2% is at 12.9 Should be 12.0
CO 8ppm
Ratio 0.0001
Smoke 0
The only thing I didnt check was the nozzle as I know I didnt have anything anywhere near it 1.10 45 S. So I am thinking the nozzle is completely the wrong size but by that time everything was red hot and it was 7 o clock. So going back with correct nozzle and servicing it whilst I am there.
So after all that my question is only short.
How has this boiler been working since November last year when it was last serviced. My only thought is somebody has been tinkering. Or different oil.
So pulled oil through went to fire it up explosive ignition ran for 3-5 secs started to vibrate like mad so I knew it wasnt right pressure was fine and not bouncing up and down so no air and filters were clear. Next I thought it was choked up checked combustion chamber not really dirty not enough to cause that anyway.
Asked have you got the manual (Of course they didnt that would make life far too easy) and it was to late to call tech so I looked at the air setting it was set at 16 I thought to myself most worcesters are around 3-4 I will try reducing it a bit so dropped it down to 10 and tried again explosive ignition gone but it ran then went to lock out sparking constantly so I checked photocell ran constantly so photocell fine its just not set up right.
Dropped air to around 4 ran fine checked smoking quite a bit so up to 6 when it stopped smoking so checked CO2 which was at 15% they are usually around 12% so I thought I would set it up around that the closest I could get was 12.9% otherwise it would not run it still drops out every now and then about 15mins.
So at the moment it is set up
CO2% is at 12.9 Should be 12.0
CO 8ppm
Ratio 0.0001
Smoke 0
The only thing I didnt check was the nozzle as I know I didnt have anything anywhere near it 1.10 45 S. So I am thinking the nozzle is completely the wrong size but by that time everything was red hot and it was 7 o clock. So going back with correct nozzle and servicing it whilst I am there.
So after all that my question is only short.
How has this boiler been working since November last year when it was last serviced. My only thought is somebody has been tinkering. Or different oil.